Had Apex mechanical installed my PowerShare today through Qmerit in Washington today, it was there first one ? they have done and they say they have 30 to do, everyone waiting on chargers or gateways. I hate being a Ginny ? but it wrked out fine. They did a clean instal!

Tesla Cybertruck PowerShare installed today IMG_1463
Sponsored

 

TwiztOG43

Well-known member
Joined
Oct 2, 2023
Threads
1
Messages
327
Reaction score
502
Location
Las Vegas
Vehicles
Tesla Model Y Performance, Tesla Model Y LR
Country flag
Would have looked cleaner without the flex
 

igs

Well-known member
Joined
Aug 7, 2023
Threads
45
Messages
1,183
Reaction score
1,730
Location
CA
Vehicles
CT, MX, MY
Occupation
Tesla: "To maintain service life, the battery pack should be stored at a state of charge (SOC) of 15 to 50%."
Country flag
That looks kinda sloppy. You only need one conduit going to the gateway and one conduit going to the connector.

Tesla Cybertruck PowerShare installed today 1000000434
 


Geebz

Well-known member
Joined
Aug 16, 2024
Threads
2
Messages
65
Reaction score
103
Location
Texas
Vehicles
Cybertruck
Occupation
Engineer
Country flag
That looks kinda sloppy. You only need one conduit going to the gateway and one conduit going to the connector.

1000000434.jpg
I think it depends on how many circuits.
 

Geebz

Well-known member
Joined
Aug 16, 2024
Threads
2
Messages
65
Reaction score
103
Location
Texas
Vehicles
Cybertruck
Occupation
Engineer
Country flag
They quoted me $5100 ?we’ll see when I get the bill from Qmerit
So far my experience was not so good at first. First quote was $59XX. I denied the first quote. Second quote, electrician contacted me to come out and get further details as there was a slight complexity he had to verify. He said it would be a few dollars less than $4k. I got the quote from qmerit for $4160. So I’m guessing that qmerits overhead on this is about $170, or the electrician was mistaken on his first verbal quote. I went ahead and accepted since it was close enough to what tesla credit is covering. Electrician is waiting on parts.
 
OP
OP
Ironalley

Ironalley

Well-known member
First Name
Mark
Joined
Jan 26, 2024
Threads
6
Messages
71
Reaction score
78
Location
Washington
Vehicles
Tesla Y performance
Occupation
Farmer
Country flag
That looks kinda sloppy. You only need one conduit going to the gateway and one conduit going to the connector.

1000000434.jpg
I agree, but we’re kind of stuck right now I feel
 

Kevinjbrosi

New member
First Name
Kevin
Joined
Dec 12, 2023
Threads
0
Messages
2
Reaction score
1
Location
Colleyville, TX
Vehicles
Cybertruck
Occupation
Retired
Country flag
Just received my quote from Qmerit $5928.75
Gateway $4180
Wall conn $688.75
Permit $500
Supplemental work $560 (2023 code upgrade)
 

mongo

Well-known member
Joined
May 27, 2024
Threads
5
Messages
4,521
Reaction score
5,497
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
That looks kinda sloppy. You only need one conduit going to the gateway and one conduit going to the connector.

1000000434.jpg
Agree Connector only needs one due to use of high voltage insulation on communication wires.

Regarding panel connections, NEC does not allow fused and unfused (service) conductors in the same conduit, so if that were a full panel backup (which it isn't), it would require two.
Gateway knockouts are 3/4, so they likely went that size versus drilling out the case and dealing with bending larger conduit.
However, that would be a little sus since 3/4 EMT only holds two #4 THHN, so did they run 6 AWG? If so, the UWC charging along with (up to) 48A of loads would overload the circuit...

@Ironalley, would you mind sharing photos of the main panel and Gateway breakers?

Side note: that Tesla image has three conduits leaving the Gateway. Third controls the backup switch.
 


Art138

Well-known member
First Name
Art
Joined
May 25, 2023
Threads
14
Messages
1,184
Reaction score
1,088
Location
Weston,Florida
Vehicles
MYP,Ford GT & FS CYBERBEAST
Country flag
Got my quote today… circa 5,600$. They will deduct the 4k credit(beast) leaving me with 1,600k out of pocket.. The additional 2,500k for FS series I can use for the gateway equipment. I am in S Florida.
 

fuji4

Member
First Name
Andrew
Joined
Mar 3, 2024
Threads
1
Messages
23
Reaction score
22
Location
Los Angeles
Vehicles
Model s plaid, Mercedes glk250, Land Rover LR4
Country flag
Got my quote today… circa 5,600$. They will deduct the 4k credit(beast) leaving me with 1,600k out of pocket.. The additional 2,500k for FS series I can use for the gateway equipment. I am in S Florida.
Not sure what you mean “additinal $2500.” Beasts get $4k total install credit,right?
 

cbbowlingmd

Well-known member
First Name
Bryce
Joined
Feb 18, 2020
Threads
9
Messages
74
Reaction score
175
Location
Knoxville, TN
Vehicles
CyberBeast, '63 Corvette, '32 Buick Model 86 Victoria, '51 GMC p/u
Occupation
Surgeon
Country flag
I'm just not going to pay $6000 for an install. Our utilities are buried in my neighborhood and we rarely lose power. Plus there are cheaper options to have the truck power the home if I want to later. I'll take the $2500 credit, but some cool stuff and use that $6k for a killer wrap.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
5
Messages
4,521
Reaction score
5,497
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
Not sure what you mean “additinal $2500.” Beasts get $4k total install credit,right?
$2,500 for all Foundation for Gateway and Wall Connector. $4k with Beast toward installation. Guessing the $5,600 already had GW and UWC removed.
 
OP
OP
Ironalley

Ironalley

Well-known member
First Name
Mark
Joined
Jan 26, 2024
Threads
6
Messages
71
Reaction score
78
Location
Washington
Vehicles
Tesla Y performance
Occupation
Farmer
Country flag
Agree Connector only needs one due to use of high voltage insulation on communication wires.

Regarding panel connections, NEC does not allow fused and unfused (service) conductors in the same conduit, so if that were a full panel backup (which it isn't), it would require two.
Gateway knockouts are 3/4, so they likely went that size versus drilling out the case and dealing with bending larger conduit.
However, that would be a little sus since 3/4 EMT only holds two #4 THHN, so did they run 6 AWG? If so, the UWC charging along with (up to) 48A of loads would overload the circuit...

@Ironalley, would you mind sharing photos of the main panel and Gateway breakers?

Side note: that Tesla image has three conduits leaving the Gateway. Third controls the backup switch.
They installed a 100 amp breaker for the gateway and left my old breakers in place and made spares out of them.

Tesla Cybertruck PowerShare installed today IMG_1469