This is correct. It is right on the border there at 48a (charger) 10' run. Though iirc (please correct if wrong) the NEC states that 6AWG is ok continuous at 65a * .8 = 52a. So you're good to go with 6AWG copper on a 60a breaker with a 48a continuous load!Sorry I need to add my 2 cents lol. We almost always want to install devices per the manufacturers installation instructions. The National Electrical Code (NEC) even has a section for this, NEC 110.3B.
You have taken into consideration the length of the run, so no need for a voltage drop calculation.
The other thing that most are not aware of is something the NEC defines as a continuous load. If the load on a branch circuit is continuous for 3Hrs or more, it must be derated to 80%. If my math is correct... the max (continuous) 48amps of the charger is 80% of a 60amp branch circuit (or you can do the inverse and multiply 48amps by 125%). I believe that is NEC 210.23b?
You should also consider the size limitations of the lugs you will land the wires on. Some lugs will require solid conductors.
I hope I haven't confused the issue more lol. Hey, my fellow EC's, let me know if I missed anything.
Good luck on your project!