Afternoon,
Since the Powershare 3V Gateway installs are crazy priced, I was wondering if this setup would work?
All manual, no interlock. DANGEROUS if NOT paying attention.
Normal situation (no outage)- use the Uni Wall Connector to charge Cybertruck. NACS connected to CT, NEMA 14-50 outage cable not connected to anything.
Outage situation - kill MAIN breaker, disconnect NACS from CT, connect NEMA 14-50 outage cable to 240V outlet in vault, turn on CT outlets.
Outage over - turn off CT outlets, disconnect NEMA 14-50 outage cable, turn on MAIN breaker, reconnect NACS charging cable.
The possible simplicity of this design (doubt NEC compliant), is the double use of the wires from the 60A breaker.
Please review the attached drawing and let me know if anyone sees any potential issues.
Side note: the NEMA 14-50 outage cable will have it's plug covered and stored out-of-site when not in use. No exposed live prongs on plug.
Will this work, or am I batshit crazy ?? MY main concern is the NEUTRAL connection.
Thanks !

Tesla Cybertruck Home Backup using 240V from CT Vault, would this work ?? OUTAGE
Sponsored

 

SSonnentag

Well-known member
First Name
Shawn
Joined
Feb 24, 2020
Threads
12
Messages
623
Reaction score
1,229
Location
Arizona
Vehicles
2018 MX and 2023 MYP
Occupation
IT Specialist
Country flag
Neutral and ground are tied together at the panel. Actually, they're separate bus bars in the panel, but they're tied together by the metal box itself. I think you'd need to pull power from the NEMA 14-50 plug in the bed instead of from the NACS plug. I'm guessing it takes some sort of software handshake and communication between the HPWC and the truck in order to activate reverse power flow via the NACS port.

Edit: I guess I should not only look at the diagram, but read too. I don't see any problem with your idea, other than the county not liking it. As long as the main is disconnected you're good. Just don't forget to disconnect the truck before switching that main back on. :)

Edit 2: Also, if you have solar, you'd want to throw the inverter disconnects as well.
 

Carlos Thomas

Well-known member
Joined
Nov 4, 2020
Threads
28
Messages
447
Reaction score
1,224
Location
San Antonio
Vehicles
Cybertruck
Country flag
I have a Interlock Kit, Generator Inlet Box and a RV/Generator 50 ft cable. The install of the Generator Inlet Box, New Breaker Switch with a Interlock kit was $500 installed with a permit. The cable was $279. So all in I was less than $800. Ready for the next power outage.
 

MICyber

Well-known member
Joined
Jun 29, 2024
Threads
10
Messages
325
Reaction score
360
Location
Michigan
Vehicles
2024 Cybertruck AWD Foundation
Country flag
Last edited:


jameskk

Well-known member
First Name
James
Joined
Apr 1, 2024
Threads
19
Messages
287
Reaction score
458
Location
Moore, SC
Vehicles
Cybertruck FS AWD, Ford F150 Lightning, Tesla Model Y Juniper
Country flag
yes a lot of people are doing this, including me. Unfortunately my electrician has stood me up for two appointments now.
 

Jager

Well-known member
First Name
Jeff
Joined
May 25, 2020
Threads
24
Messages
337
Reaction score
1,089
Location
Virginia
Vehicles
2024 Cybertruck AWD, 2022 Model 3 LR AWD
Country flag
Utilizing the Cybertruck's 240v bed outlet to provide emergency home backup power is very straightforward, and something that a lot of us will be doing because of the outrageous quotes coming out of Qmerit.

But backfeeding into the panel is both illegal and extremely ill-advised. For good reason.

Use a transfer switch. Or use an interlock. People running generators have been doing this forever. It's not hard. And it's not particularly expensive.