4 AWG or 6 AWG copper wire for 60A 2pole breaker?

Vuong785

Member
Joined
May 22, 2024
Threads
3
Messages
15
Reaction score
4
Location
dallas, tx
Vehicles
cybertruck
Country flag
Should I use 6AWG conductors for a 10’ run for the direct wired 60A breaker? :unsure:
Sponsored

 

tmeyer3

Well-known member
First Name
Trevor
Joined
Jun 27, 2021
Threads
31
Messages
2,036
Reaction score
3,615
Location
CA
Website
www.meyerwine.com
Vehicles
Model 3, '73 GMC truck, Wrangler, Tractors
Occupation
Computer Scientist, Vintner
Country flag
4AWG copper or 3AWG aluminum for 60a.

6AWG can certainly carry up to 65a, but you shouldn't exceed the .8 load standard, making 6AWG maximum standard is 65 * .8 = 52a max recommended for up to 100' runs.

If you were going beyond 100' run, then you'd have to go even larger than 4awg.

At least that's what a qualified electrician would do.

Hope that helps.
 

CYBEAST

Well-known member
First Name
Jason
Joined
Dec 17, 2023
Threads
14
Messages
308
Reaction score
427
Location
Destin, Florida
Vehicles
Cyber Beast
Occupation
Real Estate
Country flag
Use 6 as recommended in the owners manual by Tesla. It will charge at the max rate of 48A. It doesn’t make sense on paper to the electricians but Tesla has it figured out.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,549
Reaction score
5,537
Location
SE Michigan
Vehicles
Cyberbeast
Country flag


HaulingAss

Well-known member
Joined
Oct 3, 2020
Threads
28
Messages
10,342
Reaction score
20,786
Location
Western Washington, USA
Vehicles
Cybertruck DM, 2010 F-150, 2018 Performance Model 3, 2024 Performance Model 3
Country flag
4AWG copper or 3AWG aluminum for 60a.

6AWG can certainly carry up to 65a, but you shouldn't exceed the .8 load standard, making 6AWG maximum standard is 65 * .8 = 52a max recommended for up to 100' runs.

If you were going beyond 100' run, then you'd have to go even larger than 4awg.

At least that's what a qualified electrician would do.

Hope that helps.
@mongo has the correct answer.

In general, people pay too much attention to the wire diameter, and not enough attention goes into the connections. On a run that short the wire resistance is insignificant, most of the resistance comes from the terminals. Shaping the copper ends correctly and torquing to proper specs is just as important and is where most jobs fail. It doesn't hurt, and you can get a more robust, long-lasting connection to torque to spec, back off, and retorque.

BTW, I would never use aluminum wire for charging a car (and the Tesla Wall Connector is not certified or rated for aluminum wire).
 

tmeyer3

Well-known member
First Name
Trevor
Joined
Jun 27, 2021
Threads
31
Messages
2,036
Reaction score
3,615
Location
CA
Website
www.meyerwine.com
Vehicles
Model 3, '73 GMC truck, Wrangler, Tractors
Occupation
Computer Scientist, Vintner
Country flag
You'll be fine mentioned! 4AWD I hard to conduit, but I would expect it from a contracted job.

BTW, I would never use aluminum wire for charging a car (and the Tesla Wall Connector is not certified or rated for aluminum wire).
Agreed! Is this for a charger?
 

AlmostHuman

Well-known member
Joined
May 1, 2024
Threads
7
Messages
985
Reaction score
1,349
Location
Earth
Vehicles
Model X, Cybertruck
Occupation
Human
Country flag
My recommendation is to always go larger and run something that as three wires and a ground so if you ever want to change it to something like a NEMA 14-50 you can do that later with the same cable. For example I used the following for my Wall Connectors. It does increase the price of the install and wire is silly pricey right now.

4/3 NM-B x 70' Non-Metallic Electrical Cable

https://a.co/d/cD2LggX
 
OP
OP

Vuong785

Member
Joined
May 22, 2024
Threads
3
Messages
15
Reaction score
4
Location
dallas, tx
Vehicles
cybertruck
Country flag
Thanks Wade. I agree. 4 awg is best for a 60A breaker as this is considered continuous duty. I will use MC 4/3 will cap the neutral for future NEMA 14-50. (y)(y)
 
OP
OP

Vuong785

Member
Joined
May 22, 2024
Threads
3
Messages
15
Reaction score
4
Location
dallas, tx
Vehicles
cybertruck
Country flag
4AWG copper or 3AWG aluminum for 60a.

6AWG can certainly carry up to 65a, but you shouldn't exceed the .8 load standard, making 6AWG maximum standard is 65 * .8 = 52a max recommended for up to 100' runs.

If you were going beyond 100' run, then you'd have to go even larger than 4awg.

At least that's what a qualified electrician would do.

Hope that helps.
Thank you Tmeyer3 for your advice. It is definitely easier to bend 6AWG vs. 4AWG. I am going with Southwire 4/3 MC with 3/4” connector, 3/4” single hole conduit straps and a mc bushing. I used Sigma for cabling accessories.
 


OP
OP

Vuong785

Member
Joined
May 22, 2024
Threads
3
Messages
15
Reaction score
4
Location
dallas, tx
Vehicles
cybertruck
Country flag
OP
OP

Vuong785

Member
Joined
May 22, 2024
Threads
3
Messages
15
Reaction score
4
Location
dallas, tx
Vehicles
cybertruck
Country flag
I used 6 gauge and it meets code for reasonable distances. 4 gauge is very thick and hard to work with.
You are correct. Minimum wire size recommends by Tesla is 6AWG cu for 60A. I have 10’ run so 6AWG is suffice.
 

theoldguy

Active member
First Name
Steve O
Joined
Apr 22, 2020
Threads
5
Messages
38
Reaction score
90
Location
Florida
Vehicles
AWD Cybertruck, Model 3 Mid Range, Jeep Cherokee, 1978 Chevy C/K
Country flag
Sorry I need to add my 2 cents lol. We almost always want to install devices per the manufacturers installation instructions. The National Electrical Code (NEC) even has a section for this, NEC 110.3B.
You have taken into consideration the length of the run, so no need for a voltage drop calculation.
The other thing that most are not aware of is something the NEC defines as a continuous load. If the load on a branch circuit is continuous for 3Hrs or more, it must be derated to 80%. If my math is correct... the max (continuous) 48amps of the charger is 80% of a 60amp branch circuit (or you can do the inverse and multiply 48amps by 125%). I believe that is NEC 210.23b?
You should also consider the size limitations of the lugs you will land the wires on. Some lugs will require solid conductors.
I hope I haven't confused the issue more lol. Hey, my fellow EC's, let me know if I missed anything.
 

Trekboy

Well-known member
First Name
Mark
Joined
Sep 1, 2023
Threads
0
Messages
193
Reaction score
347
Location
Redding, CA USA
Vehicles
Tesla Model 3, Cybertruck
Country flag
6 AWG copper THHN in conduit is all you need. 10AWG copper THHN for the ground. That's what I ran for my 60 amp breaker, and it passed code with flying colors. Remember, it has to be THHN in conduit, no romex at that guage.