Gen 1/2 wall connectors had switches to set the breaker rating, Gen 3 or UWC is configured through the web interface (or Tesla One app).I misunderstood earlier, I thought it was defaulting to 46 amps (from 48 amps).
This is very dangerous! Please stop using the EVSE until it is configured properly. You need to configure it to not exceed the maximum charge rate your circuit is capable of handling safely!
Relying on the charge power setting in the car to not burn your house down is not an acceptable strategy! Your circuit breaker should be tripping, but it sounds as if it's defective. Get a qualified electrician in there to look at the situation.
If the wall connector is configured appropriately, it will not allow you to exceed 80% of breaker rating.
As for the effect of voltage sag, it has the opposite effect you described. Voltage sag will deliver less charge rate since the amperage caps based on breaker rating, but higher than nominal voltage (240V) will force the wall connector to drop an amp or two to stay beneath the 11.5kW max. If I get 241-242V the wall connector will kick me back to 46/47A even though the breaker and wall connector are configured to provide 48A.
Excess voltage sag or temperature faults will kick the charge rate down as well, but usually much more significantly than the 1-2A you'll get with high voltage.
If the OP is on a 50A breaker, than his wall connector could pull 46-48A without tripping, but it definitely wouldn't be safe long term.