NEMA 14-50 GFCI breaker tripping even at 18A using Mobile Connector

pae1andonly

Well-known member
First Name
Paul
Joined
Apr 29, 2025
Threads
24
Messages
389
Reaction score
411
Location
? ??
Vehicles
2024 RAM 2500
Occupation
Retired
Country flag
I have installed many NEMA 15-50 circuits and never used a GFCI specifically for this reason. You should be just fine with a regular breaker.

important to note that you absolutely should be properly torquing electrical connections. If you don't have a torque driver (or appropriately sized torque ratchet).

also a really good idea to inspect new circuits under load with thermal cameras if you can.
In my other-than-humble opinion, this post is gold. Simple, solid advice from experience. With important safety details. Nicely done.
Sponsored

 

Zwick

Well-known member
First Name
Richard
Joined
Jun 26, 2026
Threads
0
Messages
60
Reaction score
118
Location
Middle of Texas
Vehicles
23MY, 26SAWD
Country flag
In my other-than-humble opinion, this post is gold. Simple, solid advice from experience. With important safety details. Nicely done.
Agree wholeheartedly! And that inspection should include the breaker box itself. I have seen older boxes that would technically accommodate the 50A breaker, but could not safely handle the long duration 32A load pulled by the mobile charger.
 
 