If you keep the cars out of it, and you should, then a 16 kW generator is overkill. 80% of 16 kW (you want to keep your load less than 80%) is 12.6 kW and you will, with an average draw of 1.24 kW, exceed 12.6 kW only 0.0043% of the time (less than a minute in a 2 week outage). That said I think I would be inclined to go with a 20 kW unit and consider the extra 4 kW margin with which I could charge the car if I wanted to or needed to.I have looked at the last 18 months of my usage.....I average 1.24kW per day....I do not plan on running the a/c and charging both cars at the same time.
...I think we could easily get by with a 16, 18 or 20kW generator...