Sponsored

Wiring for Tesla Charger, Powershare

Is the electrician right?


  • Total voters
    10

mongo

Well-known member
Joined
May 27, 2024
Threads
5
Messages
4,524
Reaction score
5,505
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
If the cable is NM-B 4 AWG + 8 AWG ground, from a current perspective you're ok.

But I suspect the electrician wants to update wiring to individual THNN 4 AWG conductors (2 hots) plus a 6 or 8 AWG ground and put all of it in conduit (schedule 40) as required for THHN cables.

Existing cable likely has 2 hots, 1 neutral (not used by Tesla wall connector), and a ground.

Personally I am uncomfortable with that much current flowing in wires not in a conduit.
???
NM-B is fine from every perspective when properly mounted inside. What is the reason for your lack of comfort with the NEC standards? And what does circuit ampacity gave to do with it?
 

pricedm

Well-known member
First Name
Adam
Joined
Feb 17, 2022
Threads
2
Messages
927
Reaction score
1,838
Location
Denver, Colorado, USA
Vehicles
2026 Tesla Model Y LR. 2025 Cybertruck AWD. 2023 MY and 2018 M3: retired
Occupation
IT
Country flag
???
NM-B is fine from every perspective when properly mounted inside. What is the reason for your lack of comfort with the NEC standards? And what does circuit ampacity gave to do with it?
I am uncomfortable with wires for wall connector not in a conduit.
 
OP
OP

EWELON

Well-known member
First Name
Rori
Joined
May 21, 2025
Threads
29
Messages
566
Reaction score
620
Location
Wynnewood,PA
Vehicles
2021 Model 3, 2025 Cybertruck AWD
Country flag
They keep moving the goal post. But that's What Tesla does
There are definitely YouTube vids out there (out of spec for instance) of people who have PowerShare without Powerwall installed and working. After install they, turnoff the main breaker and the CT kicks in nearly instantaneously.
 


OP
OP

EWELON

Well-known member
First Name
Rori
Joined
May 21, 2025
Threads
29
Messages
566
Reaction score
620
Location
Wynnewood,PA
Vehicles
2021 Model 3, 2025 Cybertruck AWD
Country flag
I am uncomfortable with wires for wall connector not in a conduit.
Yeah the wiring is definitely in a hard conduit when it exits the exterior wall, but within the 20ish foot run from the wall to the breaker it’s running just like every other wire in the basement. Been running that way fine for the past 5ish years.

Seems like the electrician who gave me the new PowerShare quote is trying to get (more than) a few extra bucks from me by saying a whole new big ass wire needs to run from the PowerShare gateway to the location of the new wall connector.

I’m just replacing my existing one, not adding a second one….since they also told me that they can’t just add the new connector with a short run of new cable from the old connector.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
5
Messages
4,524
Reaction score
5,505
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
I’m just replacing my existing one, not adding a second one….since they also told me that they can’t just add the new connector with a short run of new cable from the old connector.
Yes, they can (local code rules excepted). Remove WC, replace with junction box, splice, run wire to new location.
What they can't do is daisy chain.
 
OP
OP

EWELON

Well-known member
First Name
Rori
Joined
May 21, 2025
Threads
29
Messages
566
Reaction score
620
Location
Wynnewood,PA
Vehicles
2021 Model 3, 2025 Cybertruck AWD
Country flag
Yes, they can (local code rules excepted). Remove WC, replace with junction box, splice, run wire to new location.
What they can't do is daisy chain.
No daisy chain is what I mean I guess. If I wanted two chargers then I would need two “home runs” back to the circuit breaker, correct?

But if I just want one charger they can just uninstall old wall connector and replace it with new WC in the same location, correct?

Reallly appreciate everyone’s help and input.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
5
Messages
4,524
Reaction score
5,505
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
No daisy chain is what I mean I guess. If I wanted two chargers then I would need two “home runs” back to the circuit breaker, correct?

But if I just want one charger they can just uninstall old wall connector and replace it with new WC in the same location, correct?

Reallly appreciate everyone’s help and input.
If you had two Gen 3 wall connectors and no Powershare, you could share a branch circuit using Group Power Management. Not sure if Powershare and Group Power Management can co-exist.

Tesla Cybertruck Wiring for Tesla Charger, Powershare SmartSelect_20250522_122813_Firefox


For your setup, swapping the old for the UWC makes sense.
 

OldDirtyRobot

Well-known member
Joined
Apr 2, 2024
Threads
11
Messages
400
Reaction score
695
Location
Texas
Vehicles
Model Y, CT Dual Motor
Occupation
Regulatory Interpretation
Country flag
Has anyone been able to use power share to power your home I am still waiting for firmware now have my truck over a year
That is insane. Mine was activated 48 hours after install. In Texas.
 


drsaab

Active member
Joined
May 10, 2024
Threads
5
Messages
26
Reaction score
60
Location
VA
Vehicles
MS, MX, CT
Country flag
They do need to run a new control wire for powershare to the Universal charger.

Also powershare is working with tesla solar but not sure about with powerwall.
 

CyberGus

Well-known member
First Name
Gus
Joined
May 22, 2021
Threads
91
Messages
10,245
Reaction score
33,911
Location
Austin, TX
Vehicles
1981 DeLorean, 2024 Cybertruck
Occupation
IT Specialist
Country flag
Not sure if Powershare and Group Power Management can co-exist.
I specifically asked this of my installer, and they said that Powershare must be on its own branch circuit.
 

Jhodgesatmb

Well-known member
First Name
Jack
Joined
Dec 1, 2019
Threads
89
Messages
6,488
Reaction score
9,025
Location
San Francisco Bay area
Website
www.arbor-studios.com
Vehicles
Tesla Cybertruck FS AWD, Tesla Model Y LR
Occupation
Retired AI researcher
Country flag
Hey all. This is my first post. About to place my order for my CT. Doing due diligence on the PowerShare. Got connected with an electrician via the Tesla website. I already have a Model 3 that we charge without difficulty using an older generation Wall Connector. I get that I’ll need to upgrade that to a Universal Wall Connector….but the electrician is saying that they’ll need to also run a new wire from the circuit breaker to the wall connnector. Which is basically the most expensive component of the whole install. Just checking to see if anyone has had a similar recommendation. They’re saying that: “this wiring would have to be replaced. The Cybertruck has a larger battery than other Tesla models, which necessitates a higher amperage circuit. To accommodate the higher amperage, it requires a larger gauge wire to be able to accommodate the increase in power flow. Without upgrading these components you will not be able to properly charge the battery for the vehicle….”

a picture of the wire in question is attached.
Thanks for the advice. Excited to finally get this vehicle!

IMG_0272.jpeg
The control wire is required because the Gateway needs to talk with the WC directly. On mine they had to pull the wires out (in conduit under my driveway because the WC is on the other side) and then run them back with the control wire.

all (modern) Teslas max out at 48 amps on a 240v circuit and a 60-amp breaker. If your wire is suited right for a 240v/60-a service you are fine. The control wire is separate.
Sponsored

 
 








Top