mongo
Well-known member
- Joined
- May 27, 2024
- Threads
- 5
- Messages
- 4,524
- Reaction score
- 5,505
- Location
- SE Michigan
- Vehicles
- Cyberbeast
Tesla Wall Connectors can be set from 12A to 48A charge current (15A to 60A breaker/ circuit). OP's charge limit is 40A on a 50A circuit.No and No and No
1. This is continuous long duration amp draw and that is an 80% rule or 48amp/.80=60 amps
2. Wire must be for 60 amps
3. Plug must be be for 60 amps
4. Torque wire screw and hold torque for 5sec release and in 1/2 hour re torque and re hold.
and
You can not series wire amps.
Correction
You can series wire amps but you must double the amp design.
and
That was your original question can I series wire an EV charge circuit and use the existing wires and plugs (which what you have is no per code and could cause fire)
Be Safe
Put in one of those 5 year battery operated smoke detector in your charge area.
Group power management allows safely sharing a circuit. Two can share an arbitrarily sized circuit.
No plugs allowed with Tesla Wall Connectors
Yes on proper torque for 5 seconds, but where are you getting the retorque step from?
NM-B is code approved, unless disallowed by local authority.