If it was a feeding a 6-50 outlet, it would be fine.Good points, not sure why my electrician did the 6/2 romex, I did question it but he said it was fine, also why my town approved it…..
60A breaker is code compliant under 240.4(B)So it reads like you still have the 6/2 romex from the panel to the subpanel? If so, the 60a breaker is not code compliant, and could fail to protect the romex in an overload situation.
Where's the neutral?If you want to do it right run 6/2 MC from main panel to sub panel.
Where has this always been written?It's always been written NOT to use Romex for wall connector wiring.