You just left out the entire last line of the 2023 NEC, but that's ok, you do you bro. I'll stick with what's approved in Florida, and avoid the unnecessary risk of fire, which won't be covered by insurance here if it did happen.240.4
(B) Overcurrent Devices Rated 800 Amperes or Less.
The next higher standard overcurrent device rating (above the ampacity of the conductors being protected) shall be permitted to be used, provided all of the following conditions are met:
(1) The conductors being protected are not part of a branch circuit supplying more than one receptacle for cord-and-plug-connected portable loads.
(2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating adjust‐
ments).
(3) The next higher standard rating selected does not exceed 800 amperes
(1) is satisfied since the circuit is not feeding outlets
(2) is satisfied since 55A does not correspond to a standard breaker that lacks adjustment.
(3) is satisfied since 60A is less than 800A
So a 60A breaker on 6 gauge NM-B is code compliant.