I had my powershare gateway installed Monday. I have two 200 main amp panels. I had to choose one for the gateway to backup. I had an option to move important circuits to the one panel that would be backed up. The installer put the gateway inside on the wall where service entered the house and put one 200 amp breaker in the gateway. Now one of my main lines pass through the gateway breaker to one of my main panels. All of the circuits in that main panel are backed up but I have to not use excessive power during power outages.
Sponsored

 

mongo

Well-known member
Joined
May 27, 2024
Threads
5
Messages
4,521
Reaction score
5,497
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
I spoke to the installer again and was told from him that the powershare gateway is rated at 200A but for the light loads install you'd only get 100A to work with. 60 Amps (charger will take 48A) goes to the CT for the charging, and therefore I'd only have the remainder to work with which may be about 6 20 amp circuits I can have.

If they are trying to put anything like the AC, than a 2" conduit would be needed to run the line.

The installer literally goes off the line item from the Qmerit quote where it states up to 10 circuits.
6 20A circuits is about right, but the reason is a little different.
That should probably be 100A of backed up load. UWC / Cybertruck is the source during Powershare, not a load.
48A continuous available @240V / 80% = 120A @ 120V
Or 60A input breaker x2 -> 3x20A output breaker x2
 
OP
OP

UrNameSux2

Active member
Joined
Dec 11, 2023
Threads
2
Messages
27
Reaction score
8
Location
San Diego
Vehicles
Yes
Country flag
Has anyone been able to get a Tesla certified installer to perform the powershare installation outside of Qmerit and was able to get the Tesla certified installer the 2-4k voucher and equipment that came with the early FS orders? If you can share your experience or steps that would be great.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
5
Messages
4,521
Reaction score
5,497
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
Has anyone been able to get a Tesla certified installer to perform the powershare installation outside of Qmerit and was able to get the Tesla certified installer the 2-4k voucher and equipment that came with the early FS orders? If you can share your experience or steps that would be great.
There are such success stories:
https://www.cybertruckownersclub.co...charges-pricing-powershare.24992/#post-419441

https://www.cybertruckownersclub.co...it-from-easy-powershare-installs.24448/page-5
 


Djinndjinn

Well-known member
Joined
May 15, 2020
Threads
23
Messages
163
Reaction score
213
Location
Pennsylvania
Vehicles
Models S, Cybertruck
Country flag
Our system was setup yesterday - our installer's first. The external power (PP&L) was routed directly into the gateway. I have 2 concerns.
1. there is no way to shut off the external power before it hits the gateway
2. there is no way to simulate a power outage because there is no breaker to turn off before the gateway
(the existing 200 amp master breaker in the breaker box still exists, so we can shut off power to the breaker box, but that is AFTER the gateway).

Questions:
For our configuration - 200 amp service, whole house (whole panel) backup, direct feed from outside power to gateway ...
1. should there be a 200 amp breaker installed in the gateway just before the attachment of the external power?
2. is this breaker an option (ie only needed if you want to simulate a power outage) or a necessity (safety issue, so eg a power surge won't fry the gateway)?

Sorry, not an electrician ... any thoughts appreciated!
 

mongo

Well-known member
Joined
May 27, 2024
Threads
5
Messages
4,521
Reaction score
5,497
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
1. should there be a 200 amp breaker installed in the gateway just before the attachment of the external power?
[Edit: I am not an electrician, codes vary by region.]
YES!
2. is this breaker an option (ie only needed if you want to simulate a power outage) or a necessity (safety issue, so eg a power surge won't fry the gateway)?
NOT OPTIONAL, it is required by code! And Tesla installation manual.
Tesla Cybertruck Powershare Gateway Circuit Breakers? SmartSelect_20241016_092855_Firefox


Dare I ask, did they convert your main panel to a subpanel? (Separate neutral and ground)

https://energylibrary.tesla.com/doc...UID-6A472F9F-13F3-4019-ABDD-C9BDE2CDEC38.html
 
Last edited:

Djinndjinn

Well-known member
Joined
May 15, 2020
Threads
23
Messages
163
Reaction score
213
Location
Pennsylvania
Vehicles
Models S, Cybertruck
Country flag
I see an instruction video that if a breaker is installed, that “neutral to ground bonding screw must remain intact, and all other panels must have ground and neutral isolated”. Means nothing to me, but hopefully it means something to my installer. I will check with them. thanks.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
5
Messages
4,521
Reaction score
5,497
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
I see an instruction video that if a breaker is installed, that “neutral to ground bonding screw must remain intact, and all other panels must have ground and neutral isolated”. Means nothing to me, but hopefully it means something to my installer. I will check with them. thanks.
Exactly, there must only be one connection from neutral to ground in the system, and that goes at the service disconnect, which the gateway should be (via main breaker) as the first thing after the meter.
The main panel used to be the disconnect and bond point.
 


CyberGus

Well-known member
First Name
Gus
Joined
May 22, 2021
Threads
91
Messages
10,238
Reaction score
33,892
Location
Austin, TX
Vehicles
1981 DeLorean, 2024 Cybertruck
Occupation
IT Specialist
Country flag

mongo

Well-known member
Joined
May 27, 2024
Threads
5
Messages
4,521
Reaction score
5,497
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
The "Service Disconnect" switch is between the Gateway and the main incoming service. Switching it off simulates a power failure.

I shot a short video of my PowerShare test:

https://www.cybertruckownersclub.com/forum/threads/my-powershare-experience.20471/post-361797
Right, but they don't have that breaker (it doesn't come pre-installed):

should there be a 200 amp breaker installed in the gateway just before the attachment of the external power?
 

LiveFreeOrDieBob

Well-known member
First Name
Bob
Joined
Oct 13, 2022
Threads
4
Messages
123
Reaction score
131
Location
New Hampshire
Vehicles
F150, Cyberbeast
Occupation
Contact Center Consulting
Country flag
My installer fixed some other things between the service and the gateway, so maybe my situation isn’t standard. I had two meters originally - he said a long time ago in NH you would pay less $$$ for elecricity to run the electric heat in a house, so a lot of houses had dual meters. My meter was leaking so he took out the two old meters, installd one new one, and installed a 200amp shutoff outside the house between the meter and the gateway, which is what I would use to simulate an outage. Then I had to pick 8 breakers I wanted to run off the truck in the case of an outage (furnace, water pump, two freezers, a fridge and the wifi so the kids don’t melt). So my old panel was turned into a sub panel.
 

Djinndjinn

Well-known member
Joined
May 15, 2020
Threads
23
Messages
163
Reaction score
213
Location
Pennsylvania
Vehicles
Models S, Cybertruck
Country flag
Mongo, cybergus, thank you both! Our installer is coming back next week to insert the 200 amp breaker in the gateway, and also changing the neutral and ground settings in the gateway and the sub panel for that install. Then I’ll be able to flip the switch and try a simulated power outage. Really appreciate everyone’s help. Love this forum.
 
OP
OP

UrNameSux2

Active member
Joined
Dec 11, 2023
Threads
2
Messages
27
Reaction score
8
Location
San Diego
Vehicles
Yes
Country flag
I reached out to Smart Charge America to go outside of the QMerit network for an estimate. The estimated looked decent and I had spoken to their powershare specialist which was their VP. I had mentioned that I'd like one of their installers come out just to make sure that they can do the job. One thing I shouldn't have done was mention the credit. After I had mentioned the credit and one of the master electricians come onsite, they decided to change the estimates onesand increased it. Needless to say I passed.

I spend time speaking to the VP on the phone and even stated that if I had not asked for a technician to come out to ensure the job can be done and just accepted your initial estimate and signed a contract, you're telling me you would have increased price, he said yes.


These installers are just trying to take advantage of the customers knowing that there is a credit for the FS owners. It's so sad.

Literally a bait and switch tactic.