Two reasons:

1) Allows for a cleaner connection (main reason)…more room.

2) If I need to shut it off, I don’t have to walk all the way around the side/back of the property. (Not as important)
Number 2 is VERY important. See my post directly above yours.
Sponsored

 

NotMyTruck

Well-known member
Joined
Oct 4, 2024
Threads
13
Messages
216
Reaction score
420
Location
Mid Atlantic
Vehicles
none
Country flag
I am not an electrician, but here are my best answers:

1) 6 gauge wire
2)
3) 60 amp breaker
4) 400 amp service (Two 200 amp panels)
5) Two 200 amp panels with 1 Tesla Wall Charger on each panel
6) Separate Panels
7) I estimate maybe 40 feet tops
8) 48 amps
9) 48 amps
10)
11)
12)
13)

I answered the ones I could.

Here are two more photos of the carnage. They believe the culprit was the piece that is in my Wife’s hand and it arched.

IMG_0068.webp


IMG_0069.webp

Tesla installation instructions do not call for an emergency disconnect. I don’t understand the reasoning for this.
Two reasons:

1) Allows for a cleaner connection (main reason)…more room.

2) If I need to shut it off, I don’t have to walk all the way around the side/back of the property. (Not as important)

The picture you sent looks like sleeved romex. That should not be in a conduit. Review tesla installation instructions, I’m perplexed for the disconnect.
 
OP
OP
Carlos Thomas

Carlos Thomas

Well-known member
Joined
Nov 4, 2020
Threads
28
Messages
447
Reaction score
1,224
Location
San Antonio
Vehicles
Cybertruck
Country flag
The picture you sent looks like sleeved romex. That should not be in a conduit. Review tesla installation instructions, I’m perplexed for the disconnect.
Are you talking about the photo of the burned wires or the install photo inside the box? All of the conduit is running through the garage. Nothing is outside.
 

NotMyTruck

Well-known member
Joined
Oct 4, 2024
Threads
13
Messages
216
Reaction score
420
Location
Mid Atlantic
Vehicles
none
Country flag
Are you talking about the photo of the burned wires or the install photo inside the box? All of the conduit is running through the garage. Nothing is outside.
Romex should not be in conduit. Anywhere. However, if someone with IEEE can assist, there is a caveat where you can install romex in a conduit assuming it has something like 50% expansion. I don’t remember the numbers but I am sure someone here can assist.

However, I do not think this was your issue.
 
Last edited:
  • Like
Reactions: REM

hemiarch

Well-known member
First Name
Ace
Joined
Jan 22, 2025
Threads
116
Messages
8,508
Reaction score
9,793
Location
Arizona
Vehicles
2024 foundation AWD, 2024 model x
Occupation
Trauma Surgeon
Country flag
I don’t about the disconnect. Mine wasn’t installed that way and was done by a very reputable company with tons of experience but just know you can’t rely on running to the breaker. It all happens too fast. Did in my case.
 
  • Like
Reactions: REM


mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,609
Reaction score
5,603
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
Romex should not be in conduit. Anywhere. However, if someone with IEEE can assist, there is a caveat where you can install romex in a conduit assuming it has something like 50% expansion. I don’t remember the numbers but I am sure someone here can assist.

However, I do not think this was your issue.
NM-B is allowed to be in conduit for protection in dry areas.
 


mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,609
Reaction score
5,603
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
As an update, they installed an emergency disconnect box and make a cleaner connection etc. Nothing happened to the Tesla Wall Connector, but they are replacing both.

IMG_0070.jpeg


IMG_0071.jpeg
Huh. The neutral doesn't need to go through the disconnected, but it can. However, the neutral doesn't even need to exist since the WC doesn't use it.

More concerning is that the disconnect doesn't appear to be grounded.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,609
Reaction score
5,603
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
Here are two more photos of the carnage. They believe the culprit was the piece that is in my Wife’s hand and it arched.

Tesla Cybertruck Almost Burned my House Down... Thoughts / Theories? img_0068-jpeg
The culprit is whomever installed a split bolt without a divider to separate the aluminum and copper conductors...
Looks like a copper-copper, not a copper-aluminum.
Tesla Cybertruck Almost Burned my House Down... Thoughts / Theories? sw4-tin-plated-copper-split-bolt-_10-_6-awg_3
Tesla Cybertruck Almost Burned my House Down... Thoughts / Theories? shopping(1)
 

cybercricket

Well-known member
Joined
Oct 31, 2024
Threads
13
Messages
665
Reaction score
802
Location
Oregon
Vehicles
Cybertruck
Country flag
The culprit is whomever installed a split bolt without a divider to separate the aluminum and copper conductors...
Looks like a copper-copper, not a copper-aluminum.
sw4-tin-plated-copper-split-bolt-_10-_6-awg_3.jpg
shopping(1).jpg
Are these intended for this application in the first place ? There are those Polaris terminals that are insulated and can be properly torqued.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,609
Reaction score
5,603
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
Are these intended for this application in the first place ? There are those Polaris terminals that are insulated and can be properly torqued.
Yes, split bolts were made for splicing conductors. Especially handy because you can put one in the middle of an existing run. Downside is the amount of overwatch tape needed and serviceablity. The new install used Polaris for the ground.
Sponsored

 
 