100 feet of aluminum wire: fifty bucks
100 feet of copper wire: hundred and fifty bucks
Setting your house on fire: priceless
The aluminum wasn't the problem. Copper can overheat a bad connection too.

Al 4/3 SER: $1.78/ ft
Cu THHN 6,6,10 (without neutral) would be $3.74/ft + conduit
Sponsored

 

REM

Well-known member
Joined
Dec 9, 2023
Threads
14
Messages
3,584
Reaction score
6,673
Location
NC
Vehicles
2020 Model 3 Standard Range++ & Diet Cybertruck, Dual Motor
Occupation
Professional Retard
Country flag
It can't get hot though, that's the point. The only reason it got hot in this case is arcing. Here is what the AI calculated for a couple of examples :

4AWG copper @ 48A

Screenshot 2025-08-20 at 14-45-08 calculate temperature of conductor based on current - Google...png


Now 4AWG @ 48 Aluminum

Screenshot 2025-08-20 at 14-50-40 calculate temperature of conductor based on current - Google...png


I think the short copper run above was 6AWG, so just case another calculation


Screenshot 2025-08-20 at 14-52-56 calculate temperature of conductor based on current - Google...png


4AWG aluminum and 6AWG copper ended up giving the same result
Tesla Cybertruck Almost Burned my House Down... Thoughts / Theories? 1755747716252-so
 

cybercricket

Well-known member
Joined
Oct 31, 2024
Threads
13
Messages
659
Reaction score
798
Location
Oregon
Vehicles
Cybertruck
Country flag
The aluminum wasn't the problem. Copper can overheat a bad connection too.

Al 4/3 SER: $1.78/ ft
Cu THHN 6,6,10 (without neutral) would be $3.74/ft + conduit
Yeah, but as you point out the point of failure was the bolt... which wouldn't have been needed in the first place if they had a continuous run all the way to the Wall Connector... which you said they could have had, given it was a purpose-installed circuit during new construction. Even if the bolt was the correct type, a connection is a connection - potential failure point especially when human is factored in. So logically speaking CyberGus is correct.
 

CyberGus

Well-known member
First Name
Gus
Joined
May 22, 2021
Threads
91
Messages
10,252
Reaction score
33,939
Location
Austin, TX
Vehicles
1981 DeLorean, 2024 Cybertruck
Occupation
IT Specialist
Country flag
So logically speaking CyberGus is correct.
I'm printing this and putting it on my wall :LOL:

It all goes back to Mongo's caveat "when done correctly..." because I basically don't trust anyone to do it correctly. Or, if you prefer, I like to minimize the number of possible mistake vectors.

Paying extra for a continuous run of copper is cheap insurance against mistakes or malfeasance IMHO.

(To be fair, I didn't actually send a wire sample to the lab for verification lol)
 

Mr Sir

Well-known member
First Name
Michael
Joined
Feb 7, 2025
Threads
15
Messages
99
Reaction score
113
Location
23000 Sussex Hwy #162 Seaford, De 19973
Vehicles
2024 CT
Country flag
I am a retired union electrician and contractor from San Francisco. I would be called a master electrician by some. I was born into the trade and lucky enough to be trained additionally by "oldtimers".

This install has serious issues covered mostly here. Not all were mentioned even by me. Some issues missed are :

EVERY TIME ALUMINUM WIRE IS USED, IT MUST HAVE AN OXIDE INHIBITOR USED. BOTH ENDS OF WIRE.
EVERY TIME AL WIRE IS USED, IT MUST BE RE-TORKED AT REGULAR INTERVALS.

THERE NEVER WAS A RISK OF FIRE. THIS IS WHY ALL CONNECTIONS ARE IN METAL (FIRE PROOF) ENCLOSURES PER NATIONAL ELECTRICAL CODE.
 


mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,540
Reaction score
5,526
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
I am a retired union electrician and contractor from San Francisco. I would be called a master electrician by some. I was born into the trade and lucky enough to be trained additionally by "oldtimers".

This install has serious issues covered mostly here. Not all were mentioned even by me. Some issues missed are :

EVERY TIME ALUMINUM WIRE IS USED, IT MUST HAVE AN OXIDE INHIBITOR USED. BOTH ENDS OF WIRE.
EVERY TIME AL WIRE IS USED, IT MUST BE RE-TORKED AT REGULAR INTERVALS.

THERE NEVER WAS A RISK OF FIRE. THIS IS WHY ALL CONNECTIONS ARE IN METAL (FIRE PROOF) ENCLOSURES PER NATIONAL ELECTRICAL CODE.
Retorquing is NOT recommended by manufacturers nor NEC.
The box wasn't metal, but metal can get hot enough to start fires(arc welder). The box melted and burning stuff was falling out of it.
 

CyberGus

Well-known member
First Name
Gus
Joined
May 22, 2021
Threads
91
Messages
10,252
Reaction score
33,939
Location
Austin, TX
Vehicles
1981 DeLorean, 2024 Cybertruck
Occupation
IT Specialist
Country flag
I like the new micro smoke detectors and what is great they now have a 10 battery.
I like the idea, but I'd want a "smart home" detector. Depending on the configuration of your home, you might not hear an alarm blaring inside the garage.
 
First Name
MIGUEL
Joined
Aug 18, 2021
Threads
1
Messages
19
Reaction score
17
Location
DOMINICAN REPUBLIC
Vehicles
TESLA MODEL Y
Country flag
A SIDE NOTE: When the electrician installed my Tesla Wall Connector, he made a loop of extra wire coming from the panel before entering the wall connector. He stated that this was necessary for heat dissipation purposes. He said he had over 100 installations and does this with every one.
Making a loop???? this is the must stupid thing I have heard in a long time time. A loop of cable will contribute to heating is going to create a magnetic field increasing the impedance of the cable and hence the heating also longer cables means more loses.... I will go with the wright size of cable, cooper #6awg if the distance is under 100ft, and make shure all conectors are really tight, a loose conector can create a lot of heat.
 

Bridgeboy69

Well-known member
Joined
Oct 12, 2024
Threads
2
Messages
438
Reaction score
510
Location
California
Vehicles
2024 Foundation Cyberbeast & 2023 Model Y Performance
Occupation
Trying to Survive
Country flag
Spell check please so everyone here completely understands you,
I understood what he meant even with the mispellings...they were close enough 👍 😁
 


Mr Sir

Well-known member
First Name
Michael
Joined
Feb 7, 2025
Threads
15
Messages
99
Reaction score
113
Location
23000 Sussex Hwy #162 Seaford, De 19973
Vehicles
2024 CT
Country flag
Making a loop???? this is the must stupid thing I have heard in a long time time. A loop of cable will contribute to heating is going to create a magnetic field increasing the impedance of the cable and hence the heating also longer cables means more loses.... I will go with the wright size of cable, cooper #6awg if the distance is under 100ft, and make shure all conectors are really tight, a loose conector can create a lot of heat.
No disrespect Sir! I only meant it as a communication assist.
 

TickTock

Well-known member
Joined
Jul 27, 2023
Threads
41
Messages
861
Reaction score
1,839
Location
Phoenix, AZ
Vehicles
`11 Nissan Leaf; '18 Model 3; '18 Model S; '24 Beast
Occupation
Electrical Engineer
Country flag
No disrespect Sir! I only meant it as a communication assist.
This thread inspired me to do an inspection. Two Tesla chargers daisy chained master-slave. Configured for 48A max. About 3 years of service with both chargers (another 5 years with just one). 60A breaker. There is some black gunk on the ground wire which appears to be left-over electrical tape residue - not oxidation). It does appear the feed on the bottom may have gotten hot enough to glass the outer surface of the insulation on the black wire but no signs of oxidation on the copper. Any code violations or other concerns?
Tesla Cybertruck Almost Burned my House Down... Thoughts / Theories? 1757157581577-7r

Tesla Cybertruck Almost Burned my House Down... Thoughts / Theories? 1757157618903-y0

Tesla Cybertruck Almost Burned my House Down... Thoughts / Theories? 1757157645679-kr
 

Aces-Truck

Well-known member
First Name
Kevin
Joined
Apr 25, 2020
Threads
11
Messages
243
Reaction score
332
Location
Snohomish County, WA
Vehicles
2024 AWD Cybertruck, 2025 MY
Occupation
Mechanical Engineer
Country flag
This thread inspired me to do an inspection. Two Tesla chargers daisy chained master-slave. Configured for 48A max. About 3 years of service with both chargers (another 5 years with just one). 60A breaker. There is some black gunk on the ground wire which appears to be left-over electrical tape residue - not oxidation). It does appear the feed on the bottom may have gotten hot enough to glass the outer surface of the insulation on the black wire but no signs of oxidation on the copper. Any code violations or other concerns?
1757157581577-7r.png

1757157618903-y0.png

1757157645679-kr.png
Did you re-torq the terminals, at 50 in-lb? If so, did the screws rotate, in order to again meet the torq spec?
 

mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,540
Reaction score
5,526
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
This thread inspired me to do an inspection. Two Tesla chargers daisy chained master-slave. Configured for 48A max. About 3 years of service with both chargers (another 5 years with just one). 60A breaker. There is some black gunk on the ground wire which appears to be left-over electrical tape residue - not oxidation). It does appear the feed on the bottom may have gotten hot enough to glass the outer surface of the insulation on the black wire but no signs of oxidation on the copper. Any code violations or other concerns?
1757157581577-7r.webp

1757157618903-y0.webp

1757157645679-kr.webp
Only the Universal Wall Connector has the double lugs for pass through
Tesla Cybertruck Almost Burned my House Down... Thoughts / Theories? SmartSelect_20250906_075122_Firefox

There should probably be a grommet or at least more sheathing
Tesla Cybertruck Almost Burned my House Down... Thoughts / Theories? SmartSelect_20250906_074641_Firefox


Edit :
Further, that is NM-B so needs to be 4 AWG, and the terminals have a max gauge of 4, so doubling up violates that spec also.