TLDR; scroll down to see a 15kW dual inverter solar panel array stay online during a power outage thanks to Powershare

The story:

March 2024, I took delivery of my truck. It was obviously a very early build with vin in the 4xxx so I knew I was gonna have to work out the early adopter kinks. Like some others, I immediately tried getting and installing the Powershare system but it was a headache all around. I got a grotesque quote from the only installer Tesla trained for these installs and decided to look elsewhere. I eventually convinced a Tesla certified electrician to take the Powershare class and install the system for me, granted I was able to procure the 3V Gateway. A cool $3000 later, the system was up and running!

At the time, solar panels were not allowed on the supply side of the Gateway box so even after pleading with my electrician to at least set up the wiring, he left it where it was, upstream of the Gateway. That meant no solar panels during outages since I don't have fixed batteries in my home.

Fast forward to early last year when solar became supported by the Powershare system. My original electrician ghosted me so I worked with another one that was also willing to learn to do these installs. He comes over, moves the 15kW of solar into the Gateway (mind you, no one could tell us if all 15kW were allowed or if it was too much). We go test it and have no luck.

What we found out later that day was that around that same time of the install, I hit the dreaded PCS2 inverter failure.

No problem. Tesla said 2 weeks to get me in and fix the problem. Naturally that wasn't the case. Day of, after having taken a day off of work, they tell me the part isn't there yet and that I'm pushed back a month. A few weeks go by, the second PCS2 fails so now I'm charging only on DC chargers. The day comes again and they tell me another month.

I just got back the truck with 2 new PCS2 inverters and what do you know, a huge storm hit here in southern NH that took out the grid for a bit. Sure enough, both my SolarEdge inverters detected the micro-grid that the Gateway + truck create and turned on!

In this image you can see how the grid is disconnected (net usage), how my inverters are putting out about 6.5kW of AC power, how my house (Sub panel) is using 2k, and the rest is being dumped back into the truck.

I couldn't ask for a better system. I mean, I could though, as in one that wasn't proprietary and could be installed by any skilled electrician. But this will do for now.

Tesla Cybertruck Keeping Solar Panels online with Powershare during power outage Screenshot_20260623-140245
Sponsored

 

Driving D Truck

New member
First Name
Justin
Joined
Dec 23, 2025
Threads
0
Messages
1
Reaction score
0
Location
NY
Vehicles
2024 Cyberbeast
Country flag
My solar puts out more than 13kw regularly, so it’s connected outside of the powershare gateway because I wasn’t sure what would happen if the truck’s charging plus the home usage were somehow less than that amount.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,654
Reaction score
5,653
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
The specified solar limit is 11.5kW of AC production (max 60A breaker). I think that is to align with Cybertruck's maximum charge rate.
Ideally, if there is too much production, Cybertruck will shift voltage or frequency to curtail the solar inverters. It must, to handle when the pack is full. However, this control ability is probably linked to the relative capacity of the two systems. Too much solar and the truck might lose control of the micro-grid.
One could put 10kW on the backed up side and 5kW on the grid side to stay within the limits.

Tesla Cybertruck Keeping Solar Panels online with Powershare during power outage AISelect_20260702_055451_Firefox
 
OP
OP

zeke

Active member
First Name
Zeke
Joined
Mar 11, 2024
Threads
3
Messages
33
Reaction score
90
Location
New Hampshire
Vehicles
Model X Plaid, AWD Foundation Cybertruck
Occupation
Software Engineer
Country flag
The specified solar limit is 11.5kW of AC production (max 60A breaker). I think that is to align with Cybertruck's maximum charge rate.
Ideally, if there is too much production, Cybertruck will shift voltage or frequency to curtail the solar inverters. It must, to handle when the pack is full. However, this control ability is probably linked to the relative capacity of the two systems. Too much solar and the truck might lose control of the micro-grid.
One could put 10kW on the backed up side and 5kW on the grid side to stay within the limits.

AISelect_20260702_055451_Firefox.webp
Would've been nice for my installer to know this. He even talked to Tesla support and they said they weren't sure but to go with 7kW just in case.

I unfortunately can't split my inverters because their output is combined upstream, and splitting them would require a new emergency disconnect switch which means a full redesign of the system specs.

However, my inverters rarely get above 12kw since one points south and the other east. By the time the 10kw inverter is reaching peak capacity, the 5kw is already on its way down.

My plan will be then to manually turn off the 5kw inverter during outages to keep the system safe, though it'd be nice for their engineers to explain this limitation better. I like your theory about the controls not being able to handle the higher amperage, I just don't understand why that would be the case. I thought it was more about the rated capacity of the busbar than the DC control board. Maybe it's only rated for 100A and they don't want to exceed the combined theoretical maximum in the scenario where:
- the house calls for a full 100A
- the truck provides 48A (11.5kW at 240v)
- the panels produce 48A (11.5kW at 240)

In that case, you're still below the 100A busrating

But if you have solar producing 15kw, or 62A, and the house is calling for 130A, the system will work, but you may overheat that tiny busbar on the supply side.

If that's the case, I get why they put in those limits, but it's such a difficult scenario to hit that it'd be easy to stay below the threshold manually
 

mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,654
Reaction score
5,653
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
Would've been nice for my installer to know this. He even talked to Tesla support and they said they weren't sure but to go with 7kW just in case.

I unfortunately can't split my inverters because their output is combined upstream, and splitting them would require a new emergency disconnect switch which means a full redesign of the system specs.

However, my inverters rarely get above 12kw since one points south and the other east. By the time the 10kw inverter is reaching peak capacity, the 5kw is already on its way down.

My plan will be then to manually turn off the 5kw inverter during outages to keep the system safe, though it'd be nice for their engineers to explain this limitation better. I like your theory about the controls not being able to handle the higher amperage, I just don't understand why that would be the case. I thought it was more about the rated capacity of the busbar than the DC control board. Maybe it's only rated for 100A and they don't want to exceed the combined theoretical maximum in the scenario where:
- the house calls for a full 100A
- the truck provides 48A (11.5kW at 240v)
- the panels produce 48A (11.5kW at 240)

In that case, you're still below the 100A busrating

But if you have solar producing 15kw, or 62A, and the house is calling for 130A, the system will work, but you may overheat that tiny busbar on the supply side.

If that's the case, I get why they put in those limits, but it's such a difficult scenario to hit that it'd be easy to stay below the threshold manually
I can't image it's a busbar thing since the grid can supply 200A versus Powershare's 48A.

My guess it is so that Powershare can suck up all generation if needed to regulate the waveform. Similarly, it can pickup all load if the solar suddenly drops out. Not that there is any guarantee that the home isn't pulling over 11.5 kW, but that's on the user.
 


OP
OP

zeke

Active member
First Name
Zeke
Joined
Mar 11, 2024
Threads
3
Messages
33
Reaction score
90
Location
New Hampshire
Vehicles
Model X Plaid, AWD Foundation Cybertruck
Occupation
Software Engineer
Country flag
I can't image it's a busbar thing since the grid can supply 200A versus Powershare's 48A.

My guess it is so that Powershare can suck up all generation if needed to regulate the waveform. Similarly, it can pickup all load if the solar suddenly drops out. Not that there is any guarantee that the home isn't pulling over 11.5 kW, but that's on the user.
But that busbar is independent from the 200A path from the grid to the main service. I was just looking at the gateway box itself and it's isolated from the load and line sides so it might still be the case.

Otherwise, what happens if the truck is at 100% charge? it can't take ANY charge at that point so it wouldn't matter how little solar you have. It should be doing a frequency shift to make the panels shut down at that point.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,654
Reaction score
5,653
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
But that busbar is independent from the 200A path from the grid to the main service. I was just looking at the gateway box itself and it's isolated from the load and line sides so it might still be the case.

Otherwise, what happens if the truck is at 100% charge? it can't take ANY charge at that point so it wouldn't matter how little solar you have. It should be doing a frequency shift to make the panels shut down at that point.
The panelboard is 200A bus rated, with the recommendation to put generation toward the top.

Yeah, Cybertruck needs to shift V or F to curtail production and likely has a bit of buffer and/or tapers charging early to prevent the full solar output while going from 99 to 100%.
 

wappone

Member
First Name
Giovanni
Joined
Dec 20, 2024
Threads
2
Messages
22
Reaction score
33
Location
Florida
Vehicles
cybertruck
Occupation
self employed
Country flag
😞 Me hoping to get some updates about us powerwall+solar users with regular gateway
 

cybertrok

Active member
First Name
Sebastian
Joined
Dec 23, 2024
Threads
0
Messages
40
Reaction score
32
Location
Toronto
Vehicles
cybertruck
Occupation
drone pilot
Country flag
TLDR; scroll down to see a 15kW dual inverter solar panel array stay online during a power outage thanks to Powershare

The story:

March 2024, I took delivery of my truck. It was obviously a very early build with vin in the 4xxx so I knew I was gonna have to work out the early adopter kinks. Like some others, I immediately tried getting and installing the Powershare system but it was a headache all around. I got a grotesque quote from the only installer Tesla trained for these installs and decided to look elsewhere. I eventually convinced a Tesla certified electrician to take the Powershare class and install the system for me, granted I was able to procure the 3V Gateway. A cool $3000 later, the system was up and running!

At the time, solar panels were not allowed on the supply side of the Gateway box so even after pleading with my electrician to at least set up the wiring, he left it where it was, upstream of the Gateway. That meant no solar panels during outages since I don't have fixed batteries in my home.

Fast forward to early last year when solar became supported by the Powershare system. My original electrician ghosted me so I worked with another one that was also willing to learn to do these installs. He comes over, moves the 15kW of solar into the Gateway (mind you, no one could tell us if all 15kW were allowed or if it was too much). We go test it and have no luck.

What we found out later that day was that around that same time of the install, I hit the dreaded PCS2 inverter failure.

No problem. Tesla said 2 weeks to get me in and fix the problem. Naturally that wasn't the case. Day of, after having taken a day off of work, they tell me the part isn't there yet and that I'm pushed back a month. A few weeks go by, the second PCS2 fails so now I'm charging only on DC chargers. The day comes again and they tell me another month.

I just got back the truck with 2 new PCS2 inverters and what do you know, a huge storm hit here in southern NH that took out the grid for a bit. Sure enough, both my SolarEdge inverters detected the micro-grid that the Gateway + truck create and turned on!

In this image you can see how the grid is disconnected (net usage), how my inverters are putting out about 6.5kW of AC power, how my house (Sub panel) is using 2k, and the rest is being dumped back into the truck.

I couldn't ask for a better system. I mean, I could though, as in one that wasn't proprietary and could be installed by any skilled electrician. But this will do for now.

Screenshot_20260623-140245.webp
Hi everyone! My electrician is actually coming this weekend to install my PowerShare this is all Chinese to me sorry for the ignorance but is there anything I should tell my electrician. I also have a solar edge system with 50 445watt panels. Please share any important information I can share with my electrician and solar edge installer this is new to them as well.

sebastian
 


mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,654
Reaction score
5,653
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
Hi everyone! My electrician is actually coming this weekend to install my PowerShare this is all Chinese to me sorry for the ignorance but is there anything I should tell my electrician. I also have a solar edge system with 50 445watt panels. Please share any important information I can share with my electrician and solar edge installer this is new to them as well.

sebastian
That's 22.5kW of potential generation on the DC side. You can have up to 11.5 kW of AC output on the backed up side of the Gateway. If the Solar Edge is multiple inverters, they might be able to split them to give Solar+Powershare .
Details are in the publicly available Powershare installation manual.
 

MilliM

Well-known member
Joined
May 7, 2020
Threads
15
Messages
142
Reaction score
197
Location
Orange County
Vehicles
Future Cybertruck Owner!
Country flag
Just chiming in to say how great this solution is. Have had my PowerShare tied into my solar for a little over a year and provides so much peace of mind, especially being in a part of SoCal where our power can be cut from time to time if the winds are too high.

Blows my mind that I have the equivalent of nearly 10 powerwalls ready to go in an emergency situation. As I’ve perhaps mentioned before, this paired with my Skywell water system, gives me extra peace of mind in case the “big one” decides to hit and interrupt our water system…only been waiting for that to hammer SoCal for pretty much my entire life.
 
OP
OP

zeke

Active member
First Name
Zeke
Joined
Mar 11, 2024
Threads
3
Messages
33
Reaction score
90
Location
New Hampshire
Vehicles
Model X Plaid, AWD Foundation Cybertruck
Occupation
Software Engineer
Country flag
I'm a scientist and an engineer. I feel like when all
Just chiming in to say how great this solution is. Have had my PowerShare tied into my solar for a little over a year and provides so much peace of mind, especially being in a part of SoCal where our power can be cut from time to time if the winds are too high.

Blows my mind that I have the equivalent of nearly 10 powerwalls ready to go in an emergency situation. As I’ve perhaps mentioned before, this paired with my Skywell water system, gives me extra peace of mind in case the “big one” decides to hit and interrupt our water system…only been waiting for that to hammer SoCal for pretty much my entire life.
Right, I forget people live in civilization most of the time :D

So the cool thing with my setup is that it allows me to go fully off-grid for extended periods of time. I live in a forest in New Hampshire, which means I can run my house independent of public utilities. I have:
- my own water well which uses negligible power (and subsequently a septic tank for sewage)
- geothermal heating and cooling, which also use very low power even down to -10F (max 3.3kw sustained)
- all EVs
- fiber, trivially kept alive by powering the ONT and my Unify system (which I could update to satellite internet in theory, but it's worse than the 2gb/s I get now)
- an all electric tractor for plowing, pushing, digging, moving, etc (15kWh and a negligible 1kw charger)

And if all else fails, I run an 80kBTU wood fireplace insert from wood I harvest each year, so that I can keep warm in the winter were my system to fail.

Anyways, my experience with Powershare has been anything but smooth, yet I wish one day for this type of system to be more mainstream and less proprietary. Fingers crossed that the R2 actually ships with 100A bidirectional charging, then we'll finally have some good competition! (the Lightning's powershare would've been cool had they not axed the truck itself)