Two reasons:

1) Allows for a cleaner connection (main reason)…more room.

2) If I need to shut it off, I don’t have to walk all the way around the side/back of the property. (Not as important)
A manual shutoff within direct sight of every WC or other EV charger is both code and a specific requirement in the Tesla installation instructions.
Sponsored

 

PungoteagueDave

Well-known member
First Name
David
Joined
Mar 2, 2025
Threads
2
Messages
951
Reaction score
1,039
Location
Boynton Beach
Vehicles
‘25 Tesla Cybertruck, ‘26 Tesla MY Launch, ‘13 Porsche C4S, ‘26 BMW R1300 GSA
Occupation
retired
Country flag
Tesla installation instructions do not call for an emergency disconnect. I don’t understand the reasoning for this.


The picture you sent looks like sleeved romex. That should not be in a conduit. Review tesla installation instructions, I’m perplexed for the disconnect.
My installer showed me the instructions indicating they had to install an emergency disconnect. The county inspector also indicated that he wouldn’t have passed it without. I had objected to giving up the wall space in my garage, as we have had 8 other WC installations in other locations without it. Must be a new thing. I get why, but in my case the main box breakers are within 20 feet of both WCs, so it seems superfluous.
 
OP
OP
Carlos Thomas

Carlos Thomas

Well-known member
Joined
Nov 4, 2020
Threads
28
Messages
447
Reaction score
1,224
Location
San Antonio
Vehicles
Cybertruck
Country flag
What a nightmare...but at least it was not a worse nightmare...
🙏

And sorry if this was already mentioned (6-pages already and I did not read everything), but Tesla literally forced me to go through Q-Merit to get a licensed electrician that they approved of to install my home charger. Maybe it was because I have a Foundation Cyberbeast that came with a Powershare Gateway....although I didn't even have them install the Powershare, only the charger.

So, anyway, I am just wondering how this could even happen if you hired a Tesla approved electrician....but obviously, in this case, I assume you didn't.

I don't want to throw any salt on your wounds...but this seems to prove the point that you should not try to save a few bucks on things like electricians. Even I was second-guessing the $1,500 install charge and contemplating paying a neighbor down the street less than half of that, but after seeing your story here, hell no. Family safety is too important to cut corners to save a few bucks.

Please don't take this the wrong way, because you didn't know, and it's not your fault, but this incident seems a perfect fit for the following meme...it's like picking up pennies in front of a steam roller...it's just not worth it...

1755616109832-s3.png
The summary version. This is a new home (new build) and the builder had two Tesla Wall Chargers installed as apart of their build out. So when we bought the home, it was already configured/live.

My guess is the two wall chargers were installed by their “normal” electrical contractor that does all of their homes.
 

REM

Well-known member
Joined
Dec 9, 2023
Threads
14
Messages
3,584
Reaction score
6,673
Location
NC
Vehicles
2020 Model 3 Standard Range++ & Diet Cybertruck, Dual Motor
Occupation
Professional Retard
Country flag
The summary version. This is a new home (new build) and the builder had two Tesla Wall Chargers installed as apart of their build out. So when we bought the home, it was already configured/live.

My guess is the two wall chargers were installed by their “normal” electrical contractor that does all of their homes.
This makes perfect sense, and the primary reason I no longer trust any tradesman without double or triple checking behind them.
 

Bridgeboy69

Well-known member
Joined
Oct 12, 2024
Threads
2
Messages
438
Reaction score
510
Location
California
Vehicles
2024 Foundation Cyberbeast & 2023 Model Y Performance
Occupation
Trying to Survive
Country flag
So when we bought the home, it was already configured/live.
Man, I am so sorry you are going through this. But at least your family is safe now.

I hope you sue the shit out of whoever is responsible for this crap.
 


mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,540
Reaction score
5,526
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
1755609319419-ta.png


Yep! In practice, it's technically correct to have an equipment ground lug for each separate enclosure for sure ... however when I am lazy and can't be bothered on my own personal stuff, I rely on the mechanically connected lug from the other equipment and the fact that he has a path to ground from the armored BX cable lol.

The amount of things that would need to go catastrophically wrong for the ground to completely fail would be infinitesimally small, and by then you very likely have much larger issues to worry about; like the tornado that twisted your house into a pretzel to make that scenario even plausible.

Having said that, if you want it done completely right, that disconnect switch should be using a grounding lug/terminal block.
Still, isn't it bad practice to rely on a downstream connection for grounding though? Sort of like not using a duplex outlet as neutral continuance for a split neutral branch circuit .
I thought BX isn't allowed as ground in new installs anyway?
 

freddms

Active member
First Name
fred
Joined
Mar 12, 2025
Threads
0
Messages
40
Reaction score
67
Location
marion ia
Vehicles
cybertruck
Occupation
retired
Country flag
Is that aluminum wire? With aluminum, or has to be torqued properly. We don't use aluminum for house wiring... it's illegal here. Has to be copper. The whole install looks a little funky, but that's just my opinion.
It does look aluminum. Are there ANY states that allow for house wiring to be aluminum?

The utility company runs aluminum to your meter - and 'sometimes' the meter to the box is aluminum but you have to be very sure you torque aluminum and use proper contact spray and/or fray the aluminum at the point of contact.

Most building codes do not allow aluminum in the house because it's so problematic.

Never the less, this size of wire should NOT be twisted (I stated this in another post). The wire needs to be seated on a connector or bushing - or mounted on a plug, or in a breaker disconnect or bus bar.
 

freddms

Active member
First Name
fred
Joined
Mar 12, 2025
Threads
0
Messages
40
Reaction score
67
Location
marion ia
Vehicles
cybertruck
Occupation
retired
Country flag
I guess “properly sized and terminated” is the real trick, eh?

But isn’t that what professionals are for? If I want it done improperly, I’ll save money and do it myself :ROFLMAO:

Most building codes to not allow for Aluminum inside the house. For the reasons you state (properly sized and terminated is a problem with aluminum that copper is not as prone to error).
 

FarAway

Well-known member
First Name
I.
Joined
Mar 30, 2022
Threads
65
Messages
866
Reaction score
1,980
Location
Central Virginia
Vehicles
TVR, Jeep Jk Sahara, Audi Q7, FS CyberBeast
Country flag
That was not installed to code. You don't twist wires that size. They need to be landed on clamps and torqued. This does NOT look like electrician work, it looks like a DYI install.

I have plugs for mine - which generally is not a good idea (more failure points). But a good electrician will get everything landed and torqued right.
I think you can use wire nuts for two 6awg, with the right wire nut?

Best practices may be another discussion... but I do not believe this violates code, unless there is a recent code change.
Tesla Cybertruck Almost Burned my House Down... Thoughts / Theories? 1755622689880-w6
 

freddms

Active member
First Name
fred
Joined
Mar 12, 2025
Threads
0
Messages
40
Reaction score
67
Location
marion ia
Vehicles
cybertruck
Occupation
retired
Country flag
I think you can use wire nuts for two 6awg, with the right wire nut?

Best practices may be another discussion... but I do not believe this violates code, unless there is a recent code change.
1755622689880-w6.png
most state codes do not allow that.
 


Sjohnson20

Well-known member
Joined
Nov 30, 2023
Threads
8
Messages
1,438
Reaction score
2,439
Location
Florida
Vehicles
Cybertruck AWD, Model Y
Country flag
I use the mobile connector with a nema 14-50 outlet. And usually I keep amps lower when charging since it's overnight and the speed doesn't matter.
 

mongo

Well-known member
Joined
May 27, 2024
Threads
6
Messages
4,540
Reaction score
5,526
Location
SE Michigan
Vehicles
Cyberbeast
Country flag
It does look aluminum. Are there ANY states that allow for house wiring to be aluminum?

The utility company runs aluminum to your meter - and 'sometimes' the meter to the box is aluminum but you have to be very sure you torque aluminum and use proper contact spray and/or fray the aluminum at the point of contact.

Most building codes do not allow aluminum in the house because it's so problematic.

Never the less, this size of wire should NOT be twisted (I stated this in another post). The wire needs to be seated on a connector or bushing - or mounted on a plug, or in a breaker disconnect or bus bar.
Michigan allows it and aluminum is commonly used for higher current branch circuits, but not under #8. The strands were not twisted by the installer, it is manufactured with the twist and then compressed.

Anti-oxidation paste isn't required unless called out by manufacturer instructions of the device. The new alloys are much better than the old ones.
 
  • Like
Reactions: REM

FarAway

Well-known member
First Name
I.
Joined
Mar 30, 2022
Threads
65
Messages
866
Reaction score
1,980
Location
Central Virginia
Vehicles
TVR, Jeep Jk Sahara, Audi Q7, FS CyberBeast
Country flag
most state codes do not allow that.
I only know Virginnia's and VA. follows NEC code and according to the National Electrical Code (NEC), specifically Article 110.14 (Electrical Connections), two 6 AWG wires can be connected with a wire nut, provided the wire nut is listed and rated for that specific combination of wire sizes and conductor materials (e.g., copper or aluminum).
 

FRUNK-IT

Member
First Name
Ray
Joined
May 21, 2025
Threads
2
Messages
21
Reaction score
48
Location
SW Florida
Vehicles
2025 Cybertruck AWD
Occupation
Fire Inspector
Country flag
hire another electrician, certified, documenting what happened and the fix
could be the missing insultation short causing the arc
or screws not to the torque spec, causing an arc
wrong gauge wire, no sure why we see stranded vs solid
the certified electrician will provide the proof

you should not do a claim with your insurance as its not your fault, rate will go up
the claim should be against the original electrician company
stranded wire in higher gauges because solid would be unusable at that size.
 

ModelXer

Well-known member
Joined
Sep 7, 2023
Threads
0
Messages
126
Reaction score
86
Location
NY
Vehicles
Model X
Country flag
It does look aluminum. Are there ANY states that allow for house wiring to be aluminum?

The utility company runs aluminum to your meter - and 'sometimes' the meter to the box is aluminum but you have to be very sure you torque aluminum and use proper contact spray and/or fray the aluminum at the point of contact.

Most building codes do not allow aluminum in the house because it's so problematic.

Never the less, this size of wire should NOT be twisted (I stated this in another post). The wire needs to be seated on a connector or bushing - or mounted on a plug, or in a breaker disconnect or bus bar.
Aluminum has a tendency to expand and contract with the heat change as loads change, thus loosening connections. The utility company failed to pull the meter and check the connections at my MIL's house when she was having electrical issues. Electrician came and pulled the meter... aluminum service wires were loose and could have caused a fire. The utility had to replace the meter box and the meter as both were badly scorched.